DECsystem-10 Power Supply Guide
Revision as of 10:25, 6 October 2026 by Josh (talk | contribs) (Set 1 table to 70% width so it sits next to the image)
DECsystem-1090: KL10 processor cabinets and MH10 memory cabinets, each with its own power control and supplies (Retro-Computing Society of Rhode Island, CC BY-SA 3.0)
Every cabinet of a DECsystem-10 has its own power control, bulk supplies and regulators, and the cabinets switch on and off together over DEC's power control bus. DEC described the supplies, their control and protection, and their adjustment in its KL10 Maintenance Guide (EK-OKL10-MG-003), its power system description for the KL10-C processor (EK-PWR20-SD-001) and its MH10 Maintenance Manual (EK-MH10-MM-003).[1][2][3] The KL10-C description was written for the DECSYSTEM-20 model 2040, whose cabinets differ in packaging from the tall DECsystem-10 cabinets; the supply and regulator types are the same families that DEC's KL10 guide lists for all KL10-based systems.[2][1][4]
Warning: these systems run from three-phase mains at up to 60 A per phase, and the KL10 processor's ECL supply stores its energy in a 3.9 farad capacitor bank. Isolate the cabinet at its power control and at the wall, and let the capacitors discharge, before working inside.[5][6]
DEC supply types and limits
DEC's field service guide gives these output limits, measured at the backplane of the option the supply powers:[1]
General power supply specifications (KL10 Maintenance Guide, general information p. 10)
Supply type Output Maximum Minimum Maximum ripple (mV)
702 Variable – – 600
703 +10 / +1.8 / −3.0 V +11.0 / +1.9 / −3.15 +9.4 / +1.7 / −2.85 300 / – / –
705 +10 / −15 V +11.0 / −16.5 +9.4 / −14.5 300 / 700
706 +50 V +54.0 +49.0 1500
723 +8 V +9.5 +7.8 600
725 −15 V −18.0 −14.7 900
728 +10 / −15 V +11.0 / −16.0 +9.5 / −14.5 700 / 700
732 Variable – – 600
739 +53 / +65 V +55 / +65 +52 / +63 250 / 250
742 / 7420 +25 / −15 / +3 V +30 / −16.5 / +3.5 +20 / −13.5 / +2.5 –
744 / 7440 +5 V +5.05 +4.95 150
745 −15 V −15.05 −14.95 450
754 +20 / −5 V +20.2 / −5.05 +19.8 / −4.95 450 / 150
761 −2 / −5.2 V No limits given –
770 +15 V +15.05 +14.95 450
778 −15 V −16.5 −14.5 700
7131 / 7131A +5 / +12 / −2 / −5.2 V +5.07 / +12.18 / −2.03 / −5.28 +4.93 / +11.82 / −1.97 / −5.12 50 / 100 / 50 / 50
[1]
Power control
The power control bus
Each cabinet has a DEC power controller (the 863 and 861 in the KL10-C processor, the 857 in MH10 memory cabinets). They are chained by a three-wire DEC power control bus: connecting line 1 to ground (line 3) turns on every cabinet on the bus, and grounding line 2 (EMERGENCY SHUTDOWN) shuts every cabinet down.[7][8] On the 857 the bus connects at J5, with J6 and J7 in parallel for the neighbouring cabinets, and a REMOTE/LOCAL switch must be at REMOTE for the cabinet to follow the processor's power switch.[7][9]
KL10 processor
The KL10-C processor takes 120/208 V or 240/416 V three-phase five-wire power, within +6% and −12% of nominal and ±1 Hz, at up to 60 A per phase at 60 Hz (30 A at 50 Hz), about 21.6 kVA. DEC asks for a supply separate from lighting and air conditioning.[5] The 863 power control applies the switched three-phase power; it lights three orange lamps for the incoming phases, and a red POWER LED on the switch panel shows switched power.[8]
Five seconds after the POWER ON switch is pressed, the 863 opens its normally closed CROBAR and POWER WARNING lines and the logic is released; at power-down CROBAR lags POWER WARNING by 5 ms. At least 13 seconds must pass between power-down and the next power-up.[8] The 863 shuts the system down and holds it off for at least 13 seconds on any of eight faults, each shown by an LED on the 863 and by the FAULT lamp on the switch panel: insufficient air flow at four sensors, an over-temperature input (not used), a tripped circuit breaker to the CPU supply, and two cooling-assembly doors open.[8] An override switch in the 863 lets maintenance staff power up through a fault; the POWER lamp then blinks.[8]
The 857 in each MH10 starts the cabinet's supplies through contactor K1. Four air-flow switches in the cabinet set an over-temperature latch that powers the cabinet down, and interlock switches on the stack and logic door panels do the same if a door is opened with power on. OVERRIDE switch S1 bypasses the air-flow shutdown (the OVERTEMP lamp still lights) and S2 bypasses the door interlocks (the PWR SWD ON lamp then flashes as a warning). A recycle delay stops the cabinet powering up again less than four seconds after power-off.[7]
The KL10 ECL supply
The KL10 CPU's ECL logic runs from −5.2 V and −2.0 V. DEC builds them in three stages:[10][11]
  • The H760 ferroresonant raw supply, with transformer primaries in three-phase delta and full-wave three-phase rectified outputs, gives −11 V at 490 A and ±15 V at 2 A. It tolerates line variation of +10% to −30%. Its ±15 V filter capacitors are C1, 50,000 µF, and C2, 30,000 µF. The H760A takes 120 V three-phase at 60 Hz and the H760B 240 V at 50 Hz, with different transformer tap connections and fan feeds.
  • The capacitor assembly (DEC 7009878) sits between the H760 and the series pass assembly: thirteen 0.3 F capacitors in parallel, 3.9 F in all, at about −11 V. On power-off it discharges through a load of a fraction of an ohm, giving 20 ms before the voltage falls to about −7.5 V so the machine can save its state.
  • The H761 regulated series pass assembly holds −5.2 V and −2.0 V with linear series-pass regulators of up to 35 A each, on G8010 (−5.2 V) and G8011 (−2.0 V) control cards with heat sinks, circuit breakers, overvoltage protection and current limiting. LEDs on the back of the control cards show that each output is present; DEC notes that apart from tripped breakers, LEDs off are the only sign that a regulator card has failed.
[10][11]
H7420 supplies and regulators
The H7420 is DEC's multipurpose bulk supply: one transformer with seven separate 25 V AC (±20%) secondaries for regulators, +8 V at 1 A and +15 V ±1.5 V at 3 A from its power control board, DC LO sensing and a 115 V convenience outlet. The H7420-A takes 120 V and the H7420-B 240 V; the jumpering for 115 V or 230 V is printed on the supply's label.[12][7][9] The regulators plug into it:
Regulators (KL10-C power system description, Table 1-3)
Regulator Output Rating Input fuse Notes
H744 +5 V ±60 mV (±50 mV in the 1985 field guide) 25 A, 150 mV ripple 15 A Ripple (switching) regulator; current limit at about 30–35 A; crowbar SCR fires above about +6.0 V
H745 −15 V ±50 mV 10 A, 450 mV ripple 15 A Used on the DIA20 and DMA20 in the KL10-C I/O cabinet
H754 +20 V and −5 V, ±5% 8 A at +20 V, 1 A at −5 V 10 A Shunt-regulated pair from a 25 V supply; overcurrent limit about 10 A; crowbar on each output
H770 +15 V – – Powers the air-flow sensors; switched on only after the fans are up to speed
[12][7][8]
The H744 and H754 crowbars short the output to ground when they fire and stay on until the capacitors have discharged, so a crowbarred regulator reads 0 V until power is cycled.[7]
MH10 power system
DEC's MH10 manual lists one 857 power control, three H7420 supplies, H744 +5 V regulators, four H754 +20/−5 V regulators and one H770 +15 V regulator. The manual gives the number of H744s as nine in its component list and seven in the regulator section.[7] Single-phase 115 V or 220 V feeds the 857, which has a rotary input-voltage selector; the top cooling fans run from the 857 and the others from 115 V outputs of the H7420s.[7]
Setting the voltages
DEC's MH10 procedure, with power on:[13]
  1. Find the regulators and backplane power tabs on the power wiring diagram D-IC-MH10-0-PW.
  2. Set +5 V at the backplane tabs with the potentiometer on top of each H744.
  3. Set +20 V with R17 on the side of each H754.
  4. Set −5 V with R21 on the top of each H754.
  5. Repeat the last two steps until neither needs further adjustment.
All three must be within ±5% at the backplane, and DEC asks for adjustments to be made at 20–30 °C ambient.[13] R17 sets the full 25 V span between +20 V and −5 V and R21 then sets −5 V to ground, which is why the two interact. For the H754 on its own, DEC's method is to power down, disconnect the load, power up, set 25 V across the outputs with R17 and −5 V to ground with R21, then reconnect the load and check again.[7]
Capacitors
DEC's power documentation gives values for the largest capacitors: the H760's 50,000 µF and 30,000 µF ±15 V filters and the thirteen 0.3 F capacitors of the ECL capacitor assembly.[11] The regulator and supply component values are on DEC's schematics, which the power system description lists by drawing number (for example D-CS-H744-0-1, D-CS-H754-0-1, D-CS-H7420-0-1 and D-CS-7009878-0-1 for the capacitor assembly) as part of the field maintenance print set.[12] Bitsavers holds drawings and illustrated parts breakdowns for several of these units.[14]
  1. ↑ 1.0 1.1 1.2 1.3 Digital Equipment Corporation, KL10 Maintenance Guide, Volume I, EK-OKL10-MG-003, April 1985, general information p. 10, "General Power Supply Specifications" (File:KL10 Maintenance Guide Volume 1 (EK-OKL10-MG-003).pdf).
  2. ↑ 2.0 2.1 Digital Equipment Corporation, DECSYSTEM-20 Power System, System Description, EK-PWR20-SD-001, April 1976, foreword (File:KL10-C Power System Description (EK-PWR20-SD-001).pdf). Scope: the KL10-C in 2040 configurations.
  3. ↑ Digital Equipment Corporation, MH10 Maintenance Manual, EK-MH10-MM-003, August 1977 (File:MH10 Core Memory Maintenance Manual (EK-MH10-MM-003).pdf).
  4. ↑ "PDP-10", Wikipedia, en.wikipedia.org/wiki/PDP-10. Packaging of the 10xx and 20xx KL10 systems.
  5. ↑ 5.0 5.1 DEC, EK-PWR20-SD-001, pp. PWR20/1-4 and 1-9, Table 1-2. KL10-C electrical requirements.
  6. ↑ DEC, EK-PWR20-SD-001, p. PWR20/3-78. Capacitor assembly discharge.
  7. ↑ 7.0 7.1 7.2 7.3 7.4 7.5 7.6 7.7 7.8 DEC, EK-MH10-MM-003, pp. 4-34 to 4-40, section 4.4.5. MH10 power system, 857 power control, air-flow and door interlocks, H7420, H744, H754 and H770.
  8. ↑ 8.0 8.1 8.2 8.3 8.4 8.5 DEC, EK-PWR20-SD-001, pp. PWR20/2-1 to 2-12. Block diagram, CROBAR and POWER WARNING timing, fault conditions, switch panel, power-fail protection and restart.
  9. ↑ 9.0 9.1 DEC, EK-MH10-MM-003, pp. 2-2 to 2-3. AC power, line voltage jumpers, 857 power control interconnection.
  10. ↑ 10.0 10.1 DEC, EK-PWR20-SD-001, pp. PWR20/2-1 to 2-3. H760, capacitor assembly and H761.
  11. ↑ 11.0 11.1 11.2 DEC, EK-PWR20-SD-001, pp. PWR20/3-74 to 3-78. H760 power supply and capacitor assembly.
  12. ↑ 12.0 12.1 12.2 DEC, EK-PWR20-SD-001, pp. PWR20/1-3 and 1-10 to 1-15, Tables 1-1, 1-3 and 1-4. Supplies, regulators, ratings and reference drawings.
  13. ↑ 13.0 13.1 DEC, EK-MH10-MM-003, pp. 5-1 to 5-3, sections 5.3 and 5.4.1. Voltage measurements and adjustment procedure.
  14. ↑ Directory listing, bitsavers.org/pdf/dec/powerSupply/, retrieved 2 October 2026: H742, H744, H745 and H754 engineering drawings and parts breakdowns, 861 power controller manual.
